Just wondered why these are not classed as "similar switchgear" to consumer units etc which are supposed to be in
non flammable enclosures in domestics.
Regards,Hz
AJJewsbury:
There is an easy solution: put a 100 mA type S RCD in the REC2 enclosure instead of the normal switch.
Just don't use Graham's metal enclosure version!
- Andy.
AJJewsbury:
There is an easy solution: put a 100 mA type S RCD in the REC2 enclosure instead of the normal switch.
Just don't use Graham's metal enclosure version!
- Andy.