Just wondered why these are not classed as "similar switchgear" to consumer units etc which are supposed to be in
non flammable enclosures in domestics.
Regards,Hz
AJJewsbury:
but the RCD would almost certainly make it "similar switchgear"
I'd still argue not - without any overcurrent protective devices there's no incoming or outgoing circuits - it's all (by the definition of a circuit) all one circuit. It can't therefore be a distribution board, and thus not any particular type of distribution board that is a consumer unit, so any similarity doesn't seem at all obvious. Let alone meeting the switchgear definition's requirement for containing both main and auxiliary switching equipment.
- Andy.
AJJewsbury:
but the RCD would almost certainly make it "similar switchgear"
I'd still argue not - without any overcurrent protective devices there's no incoming or outgoing circuits - it's all (by the definition of a circuit) all one circuit. It can't therefore be a distribution board, and thus not any particular type of distribution board that is a consumer unit, so any similarity doesn't seem at all obvious. Let alone meeting the switchgear definition's requirement for containing both main and auxiliary switching equipment.
- Andy.