Wylex 100A dp isolators in plastic enclosures.

Just wondered  why these are not classed as "similar switchgear" to consumer units etc which are supposed to be in

non flammable enclosures in domestics.

                                          Regards,Hz
Parents
  • Alcomax:



     

    Did you really believe that? 



    It is TT.   411.3.1.1, 1st paragraph:  "ECP shall be connected  to a protective conductor under the specific conditions for each type of earthing system as spec'd in regs 411.4 to 411.6, of which one is TT.

    Where ADS is used, a cpc has to be run and terminated at each point in wiring (Reg 411.3.1.1).

    Is a selective quote from the last paragraph of the reg  

    So, if you provide the RCD because it's TT, you provide a CPC ... and terminate it ...

    Not so if that equipment does not need one because it is class II.    It should, or would, not be altered by anyone else [an ordinary person] to a class 1 enclosure unless the earthing system was changed to TN or the person doing the alteration decided to take advantage of 531.3.5.3.2.201 and have a class 1 [ steel ] enclosure for the upfront RCD and make a claim on the tails being double or reinforced insulation


    Yes, I'm still sticking with this one, because this piece of equipment may well be Class II, but supplies equipment which is not Class II, hence requires the cpc to each point in wiring on the way to the Class I equipment.



    But it is TT.

    531.3.5.3.2.201 slightly bent changed the usual accepted rules for ADS . A kind of patch, if you like. We are told that a condition covered by 412 group of regs [ double or re-inforced insulation] is "allowed" for single  insulated and sheathed tails in TT up to a demarcation point. It "deems them to comply" with 412 group. It is quite an exception.

    411.3.1.1, 1st paragraph:  "ECP shall be connected  to a protective conductor under the specific conditions for each type of earthing system as spec'd in regs 411.4 to 411.6. Those specific conditions include TT and the new reg 531.3.5.3.2.201.

    If you consider the tails to the consumers equipment in TT as a circuit- I assume you do from earlier comments- that circuit has double or re-inforced insulation as the "sole protective measure" [ dictated by 531.3.5.3.2.201] and 412.1.2  tells us, in general terms, this measure shall not  be used to any circuit with an earthing contact. So you cannot have an earthing contact for termination.

    This is likely an unintended consequence of the 531.3.5.3.2.201 "get out".  We are told something quite exceptional for expediency, similar perhaps to the note for 421.1.201


    Away from the issue of the material of the outboard box, there is still a limitation with the class 1 consumer unit for TT, if you are tailing directly in with no upstream RCD, as many are being encouraged to do. The new reg "get out" is flimsy as, however way anyone wants to spin it, the box is Class 1 and has earth terminals. The consumer unit is not class II.  The protective measures outlined in 412 group have defined limits of use, but for TT purposes the demarcation point dividing the "unearthed " enclosure from the "earthed" enclosure does not exist in reality.


    From experience, the REC2 is not really suitable in most instances, but they are tried and tested. They are designed for their own isolator and that is fine. You may find most, if not all, makes of RCD are not really a good fit, particularly with respect to the limited cable clamping and the way terminal entry  of the enclosure [does not]  lines up with the RCD terminals. These REC2's are cheap. There are far better non metallic enclosures, with the benefit of a lid, that are much more adaptable and fit for purpose, though you will be paying in the region of £20 + VAT for these, plus of course, the cost of the RCD.




    The regs in their current form can be read in a way that seems to recommend some  highly suspect practice.





    That's partly what I'm trying to illustrate. Let's be clear, I don't want to make a serious objection to the plastic REC2 isolator, and, if individual designers or installers believe that a plastic box with RCD meets the regs and is safe, then they should, of course follow their experience.


    It's worth considering that, if BS 7671 (and its interpretation) were too prescriptive, some installations would not be practicable. I guess it's easier to be prescriptive in the tighter parameters of small houses, for example, but other installations need thinking "outside the box".



     



     


     


    I agree with the above. People need to consider why they are doing something, how it can be done effectively and what it is going to achieve. However, we seem to have a bit of a change in direction in the regs [ for domestic , mostly at the moment ] influenced more by carelessness . That is fine for carelessness by users, but when that is maybe influenced by the habits of installers, some of the new "rules" appear, on face value, to be prescriptive. In any event I would say that is how they are applied by the various membership schemes, "deemed to comply" for low risk for compliance with membership rules - a tick box approach. So, for example, all new work has to be RCD protected [ generally]. But does the installer then not pay enough attention to fundamental principles of Chpt 13, the RCD being a bit of a safety net?  Same for metal Cu's on TT, you are encouraged to deviate from usual principles of shock protection, encouraged, instead, to applying a patch of a glorified grommet , which in reality is  no more than a gesture?
Reply
  • Alcomax:



     

    Did you really believe that? 



    It is TT.   411.3.1.1, 1st paragraph:  "ECP shall be connected  to a protective conductor under the specific conditions for each type of earthing system as spec'd in regs 411.4 to 411.6, of which one is TT.

    Where ADS is used, a cpc has to be run and terminated at each point in wiring (Reg 411.3.1.1).

    Is a selective quote from the last paragraph of the reg  

    So, if you provide the RCD because it's TT, you provide a CPC ... and terminate it ...

    Not so if that equipment does not need one because it is class II.    It should, or would, not be altered by anyone else [an ordinary person] to a class 1 enclosure unless the earthing system was changed to TN or the person doing the alteration decided to take advantage of 531.3.5.3.2.201 and have a class 1 [ steel ] enclosure for the upfront RCD and make a claim on the tails being double or reinforced insulation


    Yes, I'm still sticking with this one, because this piece of equipment may well be Class II, but supplies equipment which is not Class II, hence requires the cpc to each point in wiring on the way to the Class I equipment.



    But it is TT.

    531.3.5.3.2.201 slightly bent changed the usual accepted rules for ADS . A kind of patch, if you like. We are told that a condition covered by 412 group of regs [ double or re-inforced insulation] is "allowed" for single  insulated and sheathed tails in TT up to a demarcation point. It "deems them to comply" with 412 group. It is quite an exception.

    411.3.1.1, 1st paragraph:  "ECP shall be connected  to a protective conductor under the specific conditions for each type of earthing system as spec'd in regs 411.4 to 411.6. Those specific conditions include TT and the new reg 531.3.5.3.2.201.

    If you consider the tails to the consumers equipment in TT as a circuit- I assume you do from earlier comments- that circuit has double or re-inforced insulation as the "sole protective measure" [ dictated by 531.3.5.3.2.201] and 412.1.2  tells us, in general terms, this measure shall not  be used to any circuit with an earthing contact. So you cannot have an earthing contact for termination.

    This is likely an unintended consequence of the 531.3.5.3.2.201 "get out".  We are told something quite exceptional for expediency, similar perhaps to the note for 421.1.201


    Away from the issue of the material of the outboard box, there is still a limitation with the class 1 consumer unit for TT, if you are tailing directly in with no upstream RCD, as many are being encouraged to do. The new reg "get out" is flimsy as, however way anyone wants to spin it, the box is Class 1 and has earth terminals. The consumer unit is not class II.  The protective measures outlined in 412 group have defined limits of use, but for TT purposes the demarcation point dividing the "unearthed " enclosure from the "earthed" enclosure does not exist in reality.


    From experience, the REC2 is not really suitable in most instances, but they are tried and tested. They are designed for their own isolator and that is fine. You may find most, if not all, makes of RCD are not really a good fit, particularly with respect to the limited cable clamping and the way terminal entry  of the enclosure [does not]  lines up with the RCD terminals. These REC2's are cheap. There are far better non metallic enclosures, with the benefit of a lid, that are much more adaptable and fit for purpose, though you will be paying in the region of £20 + VAT for these, plus of course, the cost of the RCD.




    The regs in their current form can be read in a way that seems to recommend some  highly suspect practice.





    That's partly what I'm trying to illustrate. Let's be clear, I don't want to make a serious objection to the plastic REC2 isolator, and, if individual designers or installers believe that a plastic box with RCD meets the regs and is safe, then they should, of course follow their experience.


    It's worth considering that, if BS 7671 (and its interpretation) were too prescriptive, some installations would not be practicable. I guess it's easier to be prescriptive in the tighter parameters of small houses, for example, but other installations need thinking "outside the box".



     



     


     


    I agree with the above. People need to consider why they are doing something, how it can be done effectively and what it is going to achieve. However, we seem to have a bit of a change in direction in the regs [ for domestic , mostly at the moment ] influenced more by carelessness . That is fine for carelessness by users, but when that is maybe influenced by the habits of installers, some of the new "rules" appear, on face value, to be prescriptive. In any event I would say that is how they are applied by the various membership schemes, "deemed to comply" for low risk for compliance with membership rules - a tick box approach. So, for example, all new work has to be RCD protected [ generally]. But does the installer then not pay enough attention to fundamental principles of Chpt 13, the RCD being a bit of a safety net?  Same for metal Cu's on TT, you are encouraged to deviate from usual principles of shock protection, encouraged, instead, to applying a patch of a glorified grommet , which in reality is  no more than a gesture?