Just wondered why these are not classed as "similar switchgear" to consumer units etc which are supposed to be in
non flammable enclosures in domestics.
Regards,Hz
Alcomax:
If you consider the tails to the consumers equipment in TT as a circuit- I assume you do from earlier comments- that circuit has double or re-inforced insulation as the "sole protective measure" [ dictated by 531.3.5.3.2.201] and 412.1.2 tells us, in general terms, this measure shall not be used to any circuit with an earthing contact. So you cannot have an earthing contact for termination.
Alcomax:
If you consider the tails to the consumers equipment in TT as a circuit- I assume you do from earlier comments- that circuit has double or re-inforced insulation as the "sole protective measure" [ dictated by 531.3.5.3.2.201] and 412.1.2 tells us, in general terms, this measure shall not be used to any circuit with an earthing contact. So you cannot have an earthing contact for termination.