Hi folks,


We have a site welfare cabin that needs an EICR. The cabin is powered by an onboard generator, which is connected to an earth electrode.

What is lowest acceptable resistance we are looking for when conducting an earth electrode test.


Thanks for any advice you can give, I have gone through BS7671 and IET GN3 and cant find the answer..


Paul


Parents
  • Thanks you guys for all of your answers.

    The site cabin is a self contained construction site welfare unit, powered by an on board 6 kVA generator. The cabin is metallic in construction and sat on timber sleepers. The circuits inside are as usual, lights, few sockets, water heaters and general heaters, but also charging a battery.

    Currently there is an electrode installed into the ground connected to the generator via a 35mm2 conductor.

    When we undertake the EICR soon I requested that we also undertake an earth electrode test, and I wondered what reading would be deemed acceptable.


    I also am wondering what this electrode is actually achieving, seeing as the fault path on any of the circuits will not actually leave the cabin itself??
Reply
  • Thanks you guys for all of your answers.

    The site cabin is a self contained construction site welfare unit, powered by an on board 6 kVA generator. The cabin is metallic in construction and sat on timber sleepers. The circuits inside are as usual, lights, few sockets, water heaters and general heaters, but also charging a battery.

    Currently there is an electrode installed into the ground connected to the generator via a 35mm2 conductor.

    When we undertake the EICR soon I requested that we also undertake an earth electrode test, and I wondered what reading would be deemed acceptable.


    I also am wondering what this electrode is actually achieving, seeing as the fault path on any of the circuits will not actually leave the cabin itself??