Junction boxes size

Good morning,


i'm trying to find information about how to calculate junction boxes sizing by uk regulations. Can anyone help, please?


Best regards
Parents
  • Bs7671 is not a prescriptive standard  - it does not tell you how to do anything at all pretty much.  (OK that is a bit sweeping, but you get the idea I hope)

    Instead it sets technical aims - e.g. terminals shall be rated for the load they are expected to supply.

    How you achieve that , indeed if you have junction boxes at all, or make the joints at the accessories instead, is entirely a matter for you.

    It is not in that sense a wiring code.

    The 'onsite guide' is closer to a code, as containing many tried and tested recipes to reliably meet the regs in most cases.