Secondary support for luminaires: requirement or just good practice?

All,


Gripple wire style secondary support for recessed modular luminaires within ceiling grid systems; is this a requirement or just best practice? (Excluding instances where the manufacturer's installation instructions stipulate it.)


Regards,


P
Parents
  • 559.5.2. Simply requires adequate means to support the luminaire and that the ceiling is compatible with the weight imposed. 

    I have a particular interest in fire safety and many of the incident photos I have gathered over the years show buckled metal grid suspended ceilings with luminaires dangling at the end of wires liked some latter day mass hanging. 

    It would seem reasonable that a luminaire of any significant mass should not rely solely on one of those soft lay-in tiles without additional support. 

Reply
  • 559.5.2. Simply requires adequate means to support the luminaire and that the ceiling is compatible with the weight imposed. 

    I have a particular interest in fire safety and many of the incident photos I have gathered over the years show buckled metal grid suspended ceilings with luminaires dangling at the end of wires liked some latter day mass hanging. 

    It would seem reasonable that a luminaire of any significant mass should not rely solely on one of those soft lay-in tiles without additional support. 