Julien Leblanc:
Hello,
I need to install a type 1+2 SPD into the main panel of a small business building, which needs lightning protection.
The main breaker in the main panel is a 4 poles 40A MCB.
I was looking for a SPD and I found this: Schneider A9L16634.
In the technical specification sheet it says "Associated circuit breaker NG125N 80A curve C - Icu 15 kA".
I was wondering why the associated breaker needs to have such a high current (80A)? It seems i cannot ensure the selectivity of the breakers.
Could anyone explain what can happen if i use a smaller breaker, for example a 32A one for the protection of the SPD?
Thank you.