Selection of MCB for SPD protection

Hello,

I need to install a type 1+2 SPD into the main panel of a small business building, which needs lightning protection.

The main breaker in the main panel is a 4 poles 40A MCB.

I was looking for a SPD and I found this: Schneider A9L16634.

In the technical specification sheet it says "Associated circuit breaker NG125N 80A curve C - Icu 15 kA".

I was wondering why the associated breaker needs to have such a high current (80A)? It seems i cannot ensure the selectivity of the breakers.

Could anyone explain what can happen if i use a smaller breaker, for example a 32A one for the protection of the SPD?


Thank you.