How a simple job can go wrong quickly....
Not my work before I relate:
Existing 3-ph circuit breaker DB in a shop has a 30 mA 4 pole RCD belatedly fitted in a separate enclosure to provide blanket RCD protection. OK, not ideal.
Electrician asked to install extra 13 A socket-outlet in window during shop hours so padlocks off the circuit's circuit-breaker and proceeds, He lets the circuit neutral and cpc touch when fitting the socket-outlet and out trips the RCD as expected. Resets and shop keeper then announces that the card reader, till, air-con and some lights not working.
All that equipment now duff (technical term!).
For an interesting weekend quiz, what happened?
Without hindsight and the work being done during opening hours, what would you have done differently?
BOD
  • In the world of the earth fault relay, where the pick up coil and the trip are separate items, you sometimes see the current transformer sensing on all phases and neutral (well that is pretty much universal), but the breaking wired in on just the 3 phases, neutral solid.
    I have not given it much thought before this discussion, except that perhaps it was done for economy, but for this sort of thing, at the origin of an installation where later the phases are spit to 3 lots of single phase loads, it actually makes very good sense indeed. The last thing you want is a neutral contact that is not quite in time when the load is not well balanced.
  • There is another learning point here.
    When isolating a 3-phase installation (with single-phase circuits) follow the correct procedure. Open all the breakers before opening the main switch; and close them in the reverse order. Otherwise you risk the same occurrence.
  • My thinking is it relates to the 4 pole RCD with the neutral not making and/or breaking at the same time as the live conductors. Without a neutral and an unbalanced load phase voltages will float with the lightest loaded phase experiencing an excessive voltage thereby destroying or damaging electronic equipment connected.
    Could also be breaking circuits under load generating a transient which would make the case for fitting an SPD.