mapj1:
Possible, but a reverse polarity supply on 3 phase is very hard not to notice, and while near the origin shorting L1 to N does indeed over-volt L2-N and L3-N, you do not need to be many metres down the line for most of the volt drop to be in the final cct.
Chris Pearson:
From the sound of it, all of the final circuits are SP.
Reverse the polarity of a circuit on L3. Connect what looks like N to E. That goes back to the N-E link so you now have N at L3 potential. The devices on the other circuits now have phase to phase (L1-L3, L2-L3) for those few milliseconds before the RCD trips.
perspicacious:
Not my work before I relate:
Existing 3-ph circuit breaker DB in a shop has a 30 mA 4 pole RCD
Mike has it. The neutral was disconnected before the phases when the R.C.D. tripped off and the loads were subjected to 400 Volts. Even though the loads would be connected like a star connected motor, the star point being at the neutral bar, the equipment could have been damaged by a transient over Voltage if the N. of the R.C.D. opened before the L1, L2 and L3 contacts.
Z.