Earthing neutral

Former Community Member
Former Community Member
Why is it forbidden to earth the neutral at the source of a 3 wire system? 


Parents



  •  


    From my view point I don't see multiple parelled sets of 4/0 PE breaking at once. Considering all the PME supplies... 




     



    Is "4/0" a reference to AWG? About 100mm²?


    Perhaps not, but I don't think there's anything in the digram that suggests the size of the system or that conductors are to be paralleled - it could just as easily be applied to a small system - say a domestic off-grid setup with multiple sources where perhaps something closer to single 1.5mm² conductors might be the order of the day.



       - Andy.
Reply



  •  


    From my view point I don't see multiple parelled sets of 4/0 PE breaking at once. Considering all the PME supplies... 




     



    Is "4/0" a reference to AWG? About 100mm²?


    Perhaps not, but I don't think there's anything in the digram that suggests the size of the system or that conductors are to be paralleled - it could just as easily be applied to a small system - say a domestic off-grid setup with multiple sources where perhaps something closer to single 1.5mm² conductors might be the order of the day.



       - Andy.