OMS:
Take a look at table 6 in BS EN 61439 - that should tell you that the allowable temperature rise on terminals is 70K (usually the ambient is 20C) - so compliant switchgear could easily be operating at 90C terminal temperature when at full load - which will clearly melt PVC.
For the vast majority of cases the system is neither fully loaded nor constantly loaded - but it is a common mistake made by designers and then picked up by testers - where it becomes a shitstorm of acrimony and argument based entirely on "What Iffery" that has no bearing on reality.