...Pretty well any manufacturer providing BS EN 61439 compliant switchgear - although I think we are at cross purposes - I was pointing out that the switchboard terminals at full load may already be at 90C - and that impacts the cabling. I think you are suggesting the opposite ie the cable is at 90C and influencing the terminals
... many manufacturers struggle to comply with the requirements (and thus limit the cable temp to 70C, to give the switchgear some headroom
...Pretty well any manufacturer providing BS EN 61439 compliant switchgear - although I think we are at cross purposes - I was pointing out that the switchboard terminals at full load may already be at 90C - and that impacts the cabling. I think you are suggesting the opposite ie the cable is at 90C and influencing the terminals
... many manufacturers struggle to comply with the requirements (and thus limit the cable temp to 70C, to give the switchgear some headroom