Hi, I keep coming across the same issue in regards to the current carrying capacity of a XLPE/SWA cable. I always use the de-rated current carrying capacity when I am not sure if all associated equipment is rated at 90°c, which is all the time. So as an example, a 4 core 150.0mm² XLPE/SWA cable clipped direct is rated at 386 Amps from table 4E4A column 3 in BS7671:2018. A standard 4 core 150.0mm² PVC/SWA is rated at 306 Amps from table 4D4A column 3. This is a big difference! If this was protected by a 355 Amp BS 88 I would flag the conductor as being undersized.
There is a note by table 4E4A that points out Regulation 512.1.5. This is regarding compatibility and says equipment should not be connected to conductors intended to operate at a temperature exceeding 70°c unless the equipment manufacturer has confirmed that the equipment is suitable for such conditions. 99% of the time I wouldn't have the available data on site. Most circuit breakers I have checked are rated at 70°c.
Any thoughts? I just want to make sure I'm providing the correct information. I don't want to provide an observation if the conductor is ok to be rated at full capacity. Cheers in advance.