Been asked to connect up a used rangemaster all-electric cooker. No rating plate but model name is 'classic 90'. It has an induction hob.

Existing cable is 6.00mm on a 32A mcb.

Phoned the manufacturer who said it would be fine, since diversity could be applied but we would have to fit a cooker switch without a built in 13a socket and uprate the mcb to 40A.

I am a little troubled to say the least.

Comments welcome.
Parents
  • I would be a bit doubtful about telephone advice that is not part of the written instructions.

    I would be inclined to use cable and MCB size as recommended in the written instructions, if these are not to hand, they should be obtainable on line.

    A smaller cable than recommended  if correctly protected by an MCB should not be dangerous but does of course carry the risk of nuisance tripping under heavy use of the cooker.
Reply
  • I would be a bit doubtful about telephone advice that is not part of the written instructions.

    I would be inclined to use cable and MCB size as recommended in the written instructions, if these are not to hand, they should be obtainable on line.

    A smaller cable than recommended  if correctly protected by an MCB should not be dangerous but does of course carry the risk of nuisance tripping under heavy use of the cooker.