Manufacterer's advice/instructions

Been asked to connect up a used rangemaster all-electric cooker. No rating plate but model name is 'classic 90'. It has an induction hob.

Existing cable is 6.00mm on a 32A mcb.

Phoned the manufacturer who said it would be fine, since diversity could be applied but we would have to fit a cooker switch without a built in 13a socket and uprate the mcb to 40A.

I am a little troubled to say the least.

Comments welcome.
Parents
  • Former Community Member
    0 Former Community Member
    Remember that a cable (and a fuse or thermal element of an MCB) will take time to heat up - shove 50A or 60A down a 6mm² cable starting from cold and it'll take several tens of minutes to warm up to 70 degrees - by which time the oven thermostat will have started switching the oven off every few minutes and the pans will have started to boil and been turned down to a simmer setting. The '10A and 30%' rule has been used successfully for probably hundreds of millions of Christmas dinners by now (plus countless everyday meals) and seems to have been perfectly satisfactory.


    How does 433.1 fare?


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    Remember that a cable (and a fuse or thermal element of an MCB) will take time to heat up - shove 50A or 60A down a 6mm² cable starting from cold and it'll take several tens of minutes to warm up to 70 degrees - by which time the oven thermostat will have started switching the oven off every few minutes and the pans will have started to boil and been turned down to a simmer setting. The '10A and 30%' rule has been used successfully for probably hundreds of millions of Christmas dinners by now (plus countless everyday meals) and seems to have been perfectly satisfactory.


    How does 433.1 fare?


    Regards


    BOD