Manufacterer's advice/instructions

Been asked to connect up a used rangemaster all-electric cooker. No rating plate but model name is 'classic 90'. It has an induction hob.

Existing cable is 6.00mm on a 32A mcb.

Phoned the manufacturer who said it would be fine, since diversity could be applied but we would have to fit a cooker switch without a built in 13a socket and uprate the mcb to 40A.

I am a little troubled to say the least.

Comments welcome.
Parents

  • perspicacious:

    How does 433.1 fare?




    I thought that we were considering a big overload of short duration. ?

    311.1

Reply

  • perspicacious:

    How does 433.1 fare?




    I thought that we were considering a big overload of short duration. ?

    311.1