Been asked to connect up a used rangemaster all-electric cooker. No rating plate but model name is 'classic 90'. It has an induction hob.

Existing cable is 6.00mm on a 32A mcb.

Phoned the manufacturer who said it would be fine, since diversity could be applied but we would have to fit a cooker switch without a built in 13a socket and uprate the mcb to 40A.

I am a little troubled to say the least.

Comments welcome.
Parents
  • Former Community Member
    0 Former Community Member
    Who said anything about fault conditions?


    Ah, I was quoting out of the 17th: 433.1 "Every circuit shall be designed so that a small overload of long duration is unlikely to occur." and earlier editions echo the same.


    My 18th isn't to hand so apologies if I've got the wrong Reg no.


    Regards


    BOD