broadgage:
In my view, the design current should be the capacity of the circuit for socket outlet circuits. Future use is unknown and could include multiple electric heaters during central heating failure.
A bit of wiggle room can be found in various ways, for domestic and similar sized installation with a single phase supply not exceeding 100 amps, remember that continuous full load operation of multiple 32 amp circuits simply can not happen. The cut out fuse would operate first.
In the case of cleaners sockets, one work around is to reduce the number of circuits from say 4 ring finals to 2 ring finals. In such circumstances I would consider more than 100 square meters of floor area per circuit to be acceptable. The circuit can still supply about half a dozen cleaning workers ALL using vacuum cleaners at the same time. Any unforeseen use of multiple electric heaters will trip the MCB rather than risk cable damage.
2 ring finals/4 cables will reduce the derating if compared to 4 ring finals/8 cables.
If say a dozen ring finals are needed, 10 for office IT equipment, and 2 for cleaners sockets, but with a modest total load, it might be worth limiting the total loading to 100 amps by a 100 amp fuse protecting the relevant sub main. The worst reasonably foreseeable loading might then be 6 cables, each loaded to 16 amps. Remember that with 3 ring finals fully loaded, that ALL the other cables downstream of the 100 amp fuse can be ignored for de-rating purposes as they cant be carrying more than 4 amps in total. Or since the loading might be spread unequaly between the legs of each ring final, perhaps allow for three cables loaded to 20 amps each, three more loaded to 12 amps each, and ignore all others.
In the case of a lighting circuit, then IMHO a reasonable allowance for expansion should be allowed, perhaps the design load plus 50% would be reasonable.
broadgage:
In my view, the design current should be the capacity of the circuit for socket outlet circuits. Future use is unknown and could include multiple electric heaters during central heating failure.
A bit of wiggle room can be found in various ways, for domestic and similar sized installation with a single phase supply not exceeding 100 amps, remember that continuous full load operation of multiple 32 amp circuits simply can not happen. The cut out fuse would operate first.
In the case of cleaners sockets, one work around is to reduce the number of circuits from say 4 ring finals to 2 ring finals. In such circumstances I would consider more than 100 square meters of floor area per circuit to be acceptable. The circuit can still supply about half a dozen cleaning workers ALL using vacuum cleaners at the same time. Any unforeseen use of multiple electric heaters will trip the MCB rather than risk cable damage.
2 ring finals/4 cables will reduce the derating if compared to 4 ring finals/8 cables.
If say a dozen ring finals are needed, 10 for office IT equipment, and 2 for cleaners sockets, but with a modest total load, it might be worth limiting the total loading to 100 amps by a 100 amp fuse protecting the relevant sub main. The worst reasonably foreseeable loading might then be 6 cables, each loaded to 16 amps. Remember that with 3 ring finals fully loaded, that ALL the other cables downstream of the 100 amp fuse can be ignored for de-rating purposes as they cant be carrying more than 4 amps in total. Or since the loading might be spread unequaly between the legs of each ring final, perhaps allow for three cables loaded to 20 amps each, three more loaded to 12 amps each, and ignore all others.
In the case of a lighting circuit, then IMHO a reasonable allowance for expansion should be allowed, perhaps the design load plus 50% would be reasonable.