High all I am new to this forum.
I have a 95mm 4 core SWA cable running to 6 Buildings which are along way apart.
This cable is fed from a feeder pillar up hill to 5 underground joints.
Within the feeder pillar the cable is underground feeding up to 3 160amp fuses and the neutral bar.
On the cable entry water is seeping up the cable and thru the gland causing rusting of the connection plate.
When loop tested at each DB the reading range from 0.29 to 0.76.
But when IR tested L1 is 0.76 L2 is 0.26 L3 is 2.89meg
Do I need to replace the cable.