Andy88:
Curiously the guidance talks only of where the 13A socket (Allowed) is located, not the equipment which obviously can be closer
PLUS 290 or 300cm is surely within 'meansurement error'/tolerance (3.3%) ?
https://electrical.theiet.org/wiring-matters/issues/53/section-701-locations-containing-a-bath-or-shower/
"230 V 13 A socket outlets are allowed, but only if they are at least 3 m horizontally from the boundary of zone 1."
There is an additional note (that I am sure all follow ;) ) reiterating the permitted by manufacturer requirement
"Check that manufacturer’s instructions confirm that the equipment is suitable for use in the relevant zone before installation in addition to checking the IP rating."