Conduit earthing

Former Community Member
Former Community Member
On an Test and Inspection is no earth wiring in a conduit system.

Do people code C2 or C3
Parents
  • I agree with Mike and AJ but:


    In your case I would be looking at the following to give me confidence in any decision on code and length between inspections, not having seen the installation some of the questions may be irrelevant:

    1 -Is the conduit in the concrete galv or painted?

    2 - Are the visible joints in the conduit well made and painted with zinc paint or other protective coating?

    3 - Is the concrete encasing the conduit dry or damp?

    4 - Are the R2 values for all parts of the conduit all good and reasonable for the lengths involved?

    5- Are the conduit terminations at the origin well made and not subject to corrosion?

    6 - In the shower areas how is the LSF cable earths attached to the conduit?





Reply
  • I agree with Mike and AJ but:


    In your case I would be looking at the following to give me confidence in any decision on code and length between inspections, not having seen the installation some of the questions may be irrelevant:

    1 -Is the conduit in the concrete galv or painted?

    2 - Are the visible joints in the conduit well made and painted with zinc paint or other protective coating?

    3 - Is the concrete encasing the conduit dry or damp?

    4 - Are the R2 values for all parts of the conduit all good and reasonable for the lengths involved?

    5- Are the conduit terminations at the origin well made and not subject to corrosion?

    6 - In the shower areas how is the LSF cable earths attached to the conduit?