Conduit earthing

Former Community Member
Former Community Member
On an Test and Inspection is no earth wiring in a conduit system.

Do people code C2 or C3
Parents

  • sowie1959:

    On an Test and Inspection is no earth wiring in a conduit system.

    Do people code C2 or C3




    I took that as no earth and wiring is in a conduit system, I didn’t actually take it as the conduit provides a good earth, but there is not a CPC conductor run inside the conduit.


    So I retract what I said above, as I assumed the conduit was not providing an earth, and go from C2 to no code at all.


    That leaves you to figure out the appropriate recommended date for the next periodic inspection and test if you have concerns about the life expectancy of the conduit system.


    Andy Betteridge 

Reply

  • sowie1959:

    On an Test and Inspection is no earth wiring in a conduit system.

    Do people code C2 or C3




    I took that as no earth and wiring is in a conduit system, I didn’t actually take it as the conduit provides a good earth, but there is not a CPC conductor run inside the conduit.


    So I retract what I said above, as I assumed the conduit was not providing an earth, and go from C2 to no code at all.


    That leaves you to figure out the appropriate recommended date for the next periodic inspection and test if you have concerns about the life expectancy of the conduit system.


    Andy Betteridge 