On an Test and Inspection is no earth wiring in a conduit system.

Do people code C2 or C3
Parents
  • Former Community Member
    0 Former Community Member

    lyledunn:

     I might suggest that a well-constructed steel conduit system is as good, if not better than a cable with an integral cpc. 



    It will be better from a perspective of safety - for any given value of R1, the relative R2 will be very small and thus you would have a very low touch voltage by default


    Almost as good as wiring the installation in MICC


    Regards


    OMS