practical need for supp bonding in bathroom

Can anyone suggest a realistic scenario where supplementary bonding would be required in a bathroom or other 701 location? I'm failing to think of one, although I may be overlooking something blindingly obvious.


It can be omitted as long all three of these are satisfied: ADS in time; RCD present; any extr-c-p connected to main bonding.


If ADS can't be done in time by either MCB/RCD then its not legal anyway.

RCD has to be present anyway.

Water and gas pipes etc should already be main bonded if they introduce a potential.
Parents

  • wallywombat:

    Before we get too hung up about existing installations, let's consider just a new build to 18th Ed. Is there a scenario which is fully 18th compliant and which requires supp bonding?




    No, but the regulations do not just consider new-builds. They also apply to the majority of installations which are not new-builds.


    You might as well say that all new builds have plastic water services so why do the regulations still mention main bonding a metal water service.

Reply

  • wallywombat:

    Before we get too hung up about existing installations, let's consider just a new build to 18th Ed. Is there a scenario which is fully 18th compliant and which requires supp bonding?




    No, but the regulations do not just consider new-builds. They also apply to the majority of installations which are not new-builds.


    You might as well say that all new builds have plastic water services so why do the regulations still mention main bonding a metal water service.