The effectiveness of the connection of extraneous-conductive-parts in the location to the main earthing terminal may
be assessed, where necessary, by the appication of Regulation 415.2.2.
and then
415.2.2 The resistance R between simultaneously accessible exposed-conductive-parts and extraneous conductive parts shall fulfil the following condition:
R <50 V/Ia in AC systems... where Ia is the operating current in amperes (A) of the protective device or:
(i) for RCDs, Ian
(ii) for overcurrent devices, the 5 s operating current.
Not unknown for items like a cast iron soil stack, or existing metal radiators, to be not really as well bonded back to the MET as this requires, and at the same time not well enough isolated from ground to be truly considered not to be an extraneous part.
In such a case a local bond solves the issue.
The effectiveness of the connection of extraneous-conductive-parts in the location to the main earthing terminal may
be assessed, where necessary, by the appication of Regulation 415.2.2.
and then
415.2.2 The resistance R between simultaneously accessible exposed-conductive-parts and extraneous conductive parts shall fulfil the following condition:
R <50 V/Ia in AC systems... where Ia is the operating current in amperes (A) of the protective device or:
(i) for RCDs, Ian
(ii) for overcurrent devices, the 5 s operating current.
Not unknown for items like a cast iron soil stack, or existing metal radiators, to be not really as well bonded back to the MET as this requires, and at the same time not well enough isolated from ground to be truly considered not to be an extraneous part.
In such a case a local bond solves the issue.