practical need for supp bonding in bathroom

Can anyone suggest a realistic scenario where supplementary bonding would be required in a bathroom or other 701 location? I'm failing to think of one, although I may be overlooking something blindingly obvious.


It can be omitted as long all three of these are satisfied: ADS in time; RCD present; any extr-c-p connected to main bonding.


If ADS can't be done in time by either MCB/RCD then its not legal anyway.

RCD has to be present anyway.

Water and gas pipes etc should already be main bonded if they introduce a potential.
Parents
  • Former Community Member
    0 Former Community Member
    Thank you very much for your reply Geoff.  No, the light and heater don't have any exposed conductive parts. It just didn't sit well with me but I am very happy not to bond.  I was thinking about Ions conducting electricity through water and going off at a tangent, I needed nudging back into reality, thanks again.
Reply
  • Former Community Member
    0 Former Community Member
    Thank you very much for your reply Geoff.  No, the light and heater don't have any exposed conductive parts. It just didn't sit well with me but I am very happy not to bond.  I was thinking about Ions conducting electricity through water and going off at a tangent, I needed nudging back into reality, thanks again.