FAULTY SUPPLY COMPANY METER METER

I have power logged shed loads of supplies over the years to investigate if a supply company meter is faulty. I have never found a faulty meter. I have found a lot of waste, lack of understanding of what it costs to run various loads and supplies to other users from the complaints supply.


You will know from reading my posts that I had a new E& meter fitted in October and had to have a dumb meter fitted as the supply company does not provide Smart 5 hole meters. Since having the meter fitted the account bill has rocketed to something like 5 times the cost of the old meter readings.


So over the last couple of days I power logged the supply and low and behold the meter is over reading on rate 1(daytime) and under reading on rate 2 (night time).  


At first Scottish Power said I would have to pay for a check meter to be fitted and I said no I can send you my recorded readings. They have now agreed to fit a new meter in 3 weeks time and after 3 consecutive meter readings they would recalculate the bill.


So my new meter is very dumb in more ways than one.
Parents
  • With the lights all off, the CH off, no laundry or dishwashing underway, consumption right now is about 1.6 A.


    I'd expect the all-off consumption of a house with a few USB sockets and wall-wart plug in's to be more like 0.1 A, not 1.6,  the sort of PSU that fits in the body of  a plug is only 10W or so on load,. and a lot less if the load is removed from the other end. You may have half a dozen, you will not have 40 !

    If it is all in one place then 1.6A should be is quite negotiable, as nearly 400W - heated towel rail ?.

    I'd be tempted to start flicking breakers or pulling fuses to identify the circuit in question. And do not rule out that you may be supplying next door's lights as well if it is an old style  terrace with shared loft.
Reply
  • With the lights all off, the CH off, no laundry or dishwashing underway, consumption right now is about 1.6 A.


    I'd expect the all-off consumption of a house with a few USB sockets and wall-wart plug in's to be more like 0.1 A, not 1.6,  the sort of PSU that fits in the body of  a plug is only 10W or so on load,. and a lot less if the load is removed from the other end. You may have half a dozen, you will not have 40 !

    If it is all in one place then 1.6A should be is quite negotiable, as nearly 400W - heated towel rail ?.

    I'd be tempted to start flicking breakers or pulling fuses to identify the circuit in question. And do not rule out that you may be supplying next door's lights as well if it is an old style  terrace with shared loft.