Cu change before pv install.

Customer wants to install pv panels after the new cu has been fitted and I just wondered what devices to fit for it.Think the PV is 4kw,so I thought maybe a B20 mcb and a DC sensitive rcd?Thanks for any advice.

                                                Regards, hz
Parents
  • You may also find that the inverter will provide power for several tens of seconds after the mains fails. If you do not have double pole rcds / a separate CU for the solar, you may find that the CU will remain live and some loads still on, after an rcd trip. 


    Regards,


    Alan.
Reply
  • You may also find that the inverter will provide power for several tens of seconds after the mains fails. If you do not have double pole rcds / a separate CU for the solar, you may find that the CU will remain live and some loads still on, after an rcd trip. 


    Regards,


    Alan.