Cu change before pv install.

Customer wants to install pv panels after the new cu has been fitted and I just wondered what devices to fit for it.Think the PV is 4kw,so I thought maybe a B20 mcb and a DC sensitive rcd?Thanks for any advice.

                                                Regards, hz
Parents
  • The PV installer usually installs a seperate 2 or 4 way cu with a type A or B RCD exclusively for their kit as part of the installation package, along with a seperate rotary 20A isolator.

    I would consult with the PV installer first - no need to duplicate kit un-necessarily.
Reply
  • The PV installer usually installs a seperate 2 or 4 way cu with a type A or B RCD exclusively for their kit as part of the installation package, along with a seperate rotary 20A isolator.

    I would consult with the PV installer first - no need to duplicate kit un-necessarily.