Shock Likelihood at Switch.

Mornin' All,


I have just inspected and tested a renovated  old flat's wiring. The original lighting wiring in places has no circuit protective conductor. The owner has installed metal plate light switches to two positions with wooden back boxes. At these two positions there is no circuit protective conductor. The flat has a new R.C.B.O. consumer unit and all other wiring is good.


I have recommended that the switches have a C.P.C. installed (difficult and disruptive) or be changed to all insulated types.


Just what is the shock risk at these two switch positions? What is the likelihood of the metal plates becoming live due to a fault? Has anyone every seen a metal plate switch break down so that the plates becomes live?


Thanks,


Z.

Parents
  • Former Community Member
    0 Former Community Member
    I have recommended that the switches have a C.P.C. installed (difficult and disruptive) or be changed to all insulated types.

    Just what is the shock risk at these two switch positions? What is the likelihood of the metal plates becoming live due to a fault? Has anyone every seen a metal plate switch break down so that the plates becomes live?



    Your issuing of an EICR will have either deemed it satisfactory or unsatisfactory, so is this topic seeking an accomplice if you have already signed to say it is satisfactory?


    Regards


    BOD


Reply
  • Former Community Member
    0 Former Community Member
    I have recommended that the switches have a C.P.C. installed (difficult and disruptive) or be changed to all insulated types.

    Just what is the shock risk at these two switch positions? What is the likelihood of the metal plates becoming live due to a fault? Has anyone every seen a metal plate switch break down so that the plates becomes live?



    Your issuing of an EICR will have either deemed it satisfactory or unsatisfactory, so is this topic seeking an accomplice if you have already signed to say it is satisfactory?


    Regards


    BOD