Shock Likelihood at Switch.

Mornin' All,


I have just inspected and tested a renovated  old flat's wiring. The original lighting wiring in places has no circuit protective conductor. The owner has installed metal plate light switches to two positions with wooden back boxes. At these two positions there is no circuit protective conductor. The flat has a new R.C.B.O. consumer unit and all other wiring is good.


I have recommended that the switches have a C.P.C. installed (difficult and disruptive) or be changed to all insulated types.


Just what is the shock risk at these two switch positions? What is the likelihood of the metal plates becoming live due to a fault? Has anyone every seen a metal plate switch break down so that the plates becomes live?


Thanks,


Z.

Parents

  • John Peckham:

    I would always code an un-earthed light fitting or metallic light switch as a Code 2 which would make an EICR "unsatisfactory ". That is my engineering judgement ...




    John, what about an ordinary ceiling rose and pendant? The lamp holder isn't earthed and unless the loop is at the rose, the CPC just stops in its terminal. The same goes for a non-metallic switch on a non-metallic box.


    I'd give them a C3, partly because a householder might (as appears to have been the case in the OP) change them for metal fittings.


    I agree that an unearthed metal fitting is a C2, RCD-protected or otherwise.

Reply

  • John Peckham:

    I would always code an un-earthed light fitting or metallic light switch as a Code 2 which would make an EICR "unsatisfactory ". That is my engineering judgement ...




    John, what about an ordinary ceiling rose and pendant? The lamp holder isn't earthed and unless the loop is at the rose, the CPC just stops in its terminal. The same goes for a non-metallic switch on a non-metallic box.


    I'd give them a C3, partly because a householder might (as appears to have been the case in the OP) change them for metal fittings.


    I agree that an unearthed metal fitting is a C2, RCD-protected or otherwise.