perspicacious:
The installation certificate should say that the lack of a CPC is a non-compliance, to quote the ESF Best practice guide I linked to above:
10.9. On completion of the work a record of any non-compliances, including the lack of protective conductors on the lighting circuits, must made in the Comments on existing installation section of the electrical installation certificate issued to cover the work
I just checked the ESF guidance on un-earthed Class 1 fittings and their guidance is C2 and an unstatisfactory report.
Aren't these two mutually incompatible?
Regards
BOD
perspicacious:
The installation certificate should say that the lack of a CPC is a non-compliance, to quote the ESF Best practice guide I linked to above:
10.9. On completion of the work a record of any non-compliances, including the lack of protective conductors on the lighting circuits, must made in the Comments on existing installation section of the electrical installation certificate issued to cover the work
I just checked the ESF guidance on un-earthed Class 1 fittings and their guidance is C2 and an unstatisfactory report.
Aren't these two mutually incompatible?
Regards
BOD