Surge arresters really needed?

Many properties now have electronic watt hour meters both smart and regular electronic digital ones now I believe that all of these have a MOV/Varistor across the power supply input which by the very nature is across the incoming tails if that type of meter is fitted then surely an SPD won't be needed because the one in the meter will protect the installation. Am I right or am I missing something??
Parents
  • Without knowing the specifics of the internals electronics, it's difficult to say. But for example if the ELV for the electronics is supplied by a resistor divider across the LV supply, and if the SPD is on the ELV side, then it will protect the meter's electronics but not the LV supply.
Reply
  • Without knowing the specifics of the internals electronics, it's difficult to say. But for example if the ELV for the electronics is supplied by a resistor divider across the LV supply, and if the SPD is on the ELV side, then it will protect the meter's electronics but not the LV supply.