Farmboy:
Zoomup:
Farmboy:
Zoomup:...I had to make a trap in the room upstairs, which turned out to be wooden boards over other wooden boards to access the cable below with a view to lengthening one cable. I used a new 60 Amp junction box as it allows two large conductors to overlap and be secured by 4 screws...
Will it thereafter be accessible - a chance a fitted carpet gets laid?
F
Hello Farmboy,
no carpet will be laid. The floor is bare wooden boards now. If the removable TRAP was to be carpet covered, I would have written on it in pencil ELECTRICAL TRAP. I didn't do that as it would have spoiled the floor's appearance. The owner is aware of the trap.
Z.
Hi Zoomup
Thank you for clarifying your particular example.
In general, I asked the NIC about a screw joint box under fitted carpet and was told that could not reasonably be considered accessible.
Cheers
F
I asked the NIC about a screw joint box under fitted carpet and was told that could not reasonably be considered accessible.
It also leaves a bump under the carpet, and may be a trip hazard. However it is accessible with a Stanley knife if required.
Joking aside the bigger problem with anything like that under boards covered by a carpet, lino or whatever is not really accessibility, so much as knowing where it is . in the future, when the notes have been lost.
If you do not worry about inspection, and I suspect in reality most folk do not open every junction if everything checks out OK, then generally you only need to get to it when there is a problem and then, like finding a damaged section of cable, if you cannot find the problem, you may choose to isolate both ends and run a new route around it.
I have done it the other way up and used a plasterboard mounting box and cover plate in the ceiling below as a inspectable location
AJJewsbury:
I asked the NIC about a screw joint box under fitted carpet and was told that could not reasonably be considered accessible.
If you asked me, I'd say that if you gained access to the location to install the JB in the first place, it can hardly be regarded as inaccessible. Of course, things might change in the future - being tiled over or covered with glued laminate - but that's a slightly different question.
Sparkingchip:
Farmboy:
AJJewsbury:
Fitted carpets are easily removed...?... a matter of judgement I guess as to what accessible / inaccessible is - a homeowner who doesn't want their fitted carpet pulled up may disagree with you, and it's existence may get lost in the mist of time, particularly if the owner moves, but perhaps a notice at the CU may suffice.
F
You offer them the alternative, plastic minitrunking run up, across and back down the wall.
Andy B.
Chris Pearson:
As for the use of screw terminal as opposed to (MF) junction blocks - are the latter available for greater than 6 mm2 cable; and if so, are the enclosures rated for the current?
So you may be stuck with traditional junction boxes.
Chris Pearson:
AJJewsbury:
I asked the NIC about a screw joint box under fitted carpet and was told that could not reasonably be considered accessible.
If you asked me, I'd say that if you gained access to the location to install the JB in the first place, it can hardly be regarded as inaccessible. Of course, things might change in the future - being tiled over or covered with glued laminate - but that's a slightly different question.I tend to concur. It's a pain in the bottom, especially if the boards are T&G, but isn't lifting boards part of the deal?
IIRC, there was an article in https://professional-electrician.com by somebody from Wago which argued that under the floorboards is not inaccessible.
If, however, the sub-floor is sheets of board glued into place, followed by wet under floor heating, and then more boards, perhaps with a decorative or durable finish, nobody is ever going to go through that. Under those circumstances, I have made it clear that should any attention be necessary (presumably not with (MF) equipment) the only way in will be through the ceilings.
AJJewsbury:
There is a world of difference in a 40 Amp. shower load and a lighting load of a few L.E.D. lamps Andy, as well you know. The possible heating effects are totally different. You are cross threaded. There is no way that the lighting cables could contact the metal light switch plate insulted or uninsulated due to physical separation.
You never mentioned the the lighting circuit for that metal switch was dedicated to just a few LED fittings