Farmboy:
Chris Pearson:
As for the use of screw terminal as opposed to (MF) junction blocks - are the latter available for greater than 6 mm2 cable; and if so, are the enclosures rated for the current?
So you may be stuck with traditional junction boxes.Are crimps and voltage rated heat shrink not acceptable?
F
In this article they nod to the issue of interpretation of accessible.
Zoomup:
AJJewsbury:
There is a world of difference in a 40 Amp. shower load and a lighting load of a few L.E.D. lamps Andy, as well you know. The possible heating effects are totally different. You are cross threaded. There is no way that the lighting cables could contact the metal light switch plate insulted or uninsulated due to physical separation.
You never mentioned the the lighting circuit for that metal switch was dedicated to just a few LED fittings
You never asked. Just how may lights would you expect a light switch to operate in a small refurbished flat?
Z.
One may also wonder why this cable got hot and burned up its insulation. This will certainly be due to a loose connection, and probably a screw left loose or very low clamp pressure. Crimp connections are much more reliable than screws, provided the correct crimp and crimp tool is used.
I would consider crimps on a 40 Amp shower circuit cable a "no no." The 4 screw per terminal 60 Amp junction box that I used is much much better.
My current role involves a lot of domestic properties. We have, on average, one shower switch burnt out per week due to loose terminals. I have 2 other very experienced sparkies with me. We all make sure the terminals are as tight as we can get them, yet there are still failures from loose terminals that we know we have tightened properly when we installed them.