Alan Capon:
Chris Pearson:
. . . Why do Zs with the main fuse removed; and how? With your probe in the live terminal of the service head? . . .Indeed. Zs can be measured at the “customer end” of the meter tails, which is where the DNO calculate it to. This is why they tell you the length and cross sectional area of the meter tails. Measuring where you are, I am assuming you have a Class 4 tester with Class 4 leads.
Alan Capon:
Chris Pearson:
. . . Why do Zs with the main fuse removed; and how? With your probe in the live terminal of the service head? . . .Indeed. Zs can be measured at the “customer end” of the meter tails, which is where the DNO calculate it to. This is why they tell you the length and cross sectional area of the meter tails. Measuring where you are, I am assuming you have a Class 4 tester with Class 4 leads.