On the subject of pulling the DNO fuse.

There have been a couple of reports here of the DNO confronting electricians who have pulled their fuse.


It's getting closer to home, a work colleague was doing a CU change on a domestic house last week, no isolator fitted, so he pulled the fuse (no seals present).

South Nottinghamshire.


Around 90 minutes later there was a knock on the door, a guy from Western Power was investigating a power loss at the property, reported by the Smart Meter phoning home.

He gave the sparky a talking to, and warned they are getting strict in pursuing people who do it, he said meter fiddling was rife, so any loss of power is checked out asap.
Parents

  • Alan Capon:




    Measuring where you are, I am assuming you have a Class 4 tester with Class 4 leads. 


    For a Zs of 1.3 initially at the consumer unit, would the fault level justify a space suit?. I was a SAP with NOSHEB for voltages up to 275kV in days of yore.


    Jaymack




Reply

  • Alan Capon:




    Measuring where you are, I am assuming you have a Class 4 tester with Class 4 leads. 


    For a Zs of 1.3 initially at the consumer unit, would the fault level justify a space suit?. I was a SAP with NOSHEB for voltages up to 275kV in days of yore.


    Jaymack