perspicacious:
If a smart meter, presumeably the DNO would not get the notification of loss of supply
Hasn't this been thought of by interlocking the cover of the terminals?
Jaymack:
I have an ongoing situation, I started an EICR and found Zs to be 1.3 ohms for TN-S, measured with the SSE main fuse removed. SSE have eventually sent someone out and have now decided to dig up the drive and lay in a new supply. This is another case where someone (Yours truly), who is authorised to do so, has found a safety issue caused by their supply. I think that they must be in a quandary as to whether to suffer the lesser of 2 evils, by authorising registered electricians to test at their incoming supply or having a sitting problem. A further consequence is that there are 2 supplies to outdoor buildings that may now require T.T. if they supply a TN-C-S.
Chris Pearson:
. . . Why do Zs with the main fuse removed; and how? With your probe in the live terminal of the service head? . . .
Alan Capon:
Chris Pearson:
. . . Why do Zs with the main fuse removed; and how? With your probe in the live terminal of the service head? . . .Indeed. Zs can be measured at the “customer end” of the meter tails, which is where the DNO calculate it to. This is why they tell you the length and cross sectional area of the meter tails. Measuring where you are, I am assuming you have a Class 4 tester with Class 4 leads.