10.5kw Shower and Storage Heaters?
Hi,
I would be grateful for some advice regarding a potential electrical upgrade which I intend to get completed this summer when we have our kitchen and bathroom refurbished. I will engage the services of an electrician nearer the time, but wanted to explore some possibilities to help with planning the works.
A bit of context first - The property is a small ex-council 3 bed semi built in 1937 and most electrics appear to be from the 80s.
Everything is set up around economy 7 (no option for gas). Heating is delivered via 7 storage heaters, hot water comes from a cylinder with immersion element and the kitchen has a free standing electric cooker.
EON upgraded us to a smart meter when we moved in and fitted a separate non-adjustable time switch which activates the storage heaters via their own consumer units (2 in total).
The economy 7 night rate is active for 7 hours between 1:30 and 8:30 am in the summer, and 12:30 and 7:30 am in the winter.
The storage heaters collectively draw as much as 13.6 kw at peak. The 3 kw immersion is on a timer and generally used between 5:30 and 7.30 am, then a short boost 5:00 to 6:00 pm.
We don’t have a shower and would really like to fit a 10.5 kw unit when we upgrade the bathroom. This is where I have concerns – although our supply is rated at 100 amp, would I be in an overload situation if I was to shower when the storage heaters and immersion are all going together?
This is likely as we are all up and getting ready before the storage heaters switch off. Worst case scenario would be the storage heaters, immersion, hob plate and kettle are all going while the shower is active (other than these items we have very few other power demands).
I understand that principles of diversity may apply. In practice, when the storage heater circuits are first activated there is likely to be a big draw, but as we’re all in bed, by the time morning comes and we want to use the shower etc. most heaters will be up to temperature and only drawing intermittent power through thermostatic control. Of course, none of this is an issue in summer.
Should I instead consider a less power hungry 8.5 kw shower or do away with the idea and opt for better stored water and a pump (not preferred)?
Our current collection of consumer units (4) is a total mess so I will be getting quotes to have the lot upgraded. I am hoping it will be no more than 2 units, one for storage heaters the other for everything else.
I wanted to consider RCBOs instead of a dual RCD setup, but the cost may be prohibitive. I have thought about only applying the RCBOs to the main board, leaving the storage heaters protected by a single RCD. I have often seen showers on their own consumer unit but assume this wouldn’t be necessary with an appropriately sized consumer unit.
The electrician will need to install it all to meet regulation, so I may have no say in the matter on this point anyway.
Any advice or recommendations will be gladly received.
Daniel.
  • First thing to do is to ensure that you do have a 100 A supply. Just because the fuse-holder is rated at 100 A doesn't mean that that is what you have. You need to contact your DNO.
    I suspect that diversity will give you just enough wriggle room, but like others in here, I cannot give a professional opinion.
  • EON upgraded us to a smart meter when we moved in
    That is a downgrade not an upgrade. It is only for the benefit of EON not you.
    Personally I would rely on a good supply of stored water for your showers. It can all be heated up overnight on cheap rate and there is less to go wrong.
  • I would consider an automatic means to disable the storage heaters when the shower is in use.
    A suitably experienced electrician can do as follows. Control the 3 largest storage heaters via a 3 pole contactor. Fit a "shower priority unit" such that when the shower is in use, the contactor for the storage heaters is opened.
  • If you have a tank full of hot water, why do you need a 10.5kW electric shower?  A small pump feeding the shower from the hot tank will take a lot less power.
    If you have a hot water tank already and enough mains pressure, then you don’t need a pump to run a thermostatic shower. Well, as long as it’s an unvented cylinder, that is.
    I say consult a plumber about getting balanced hot/cold feeds from the existing cylinder and skip the electric shower altogether.
    It it should be a cheaper install and cheaper to run.
    Caveat: I’m neither an electrician or a plumber but have done this work in my own house. I do have a pump feeding my bathrooms but only because my well supply is a little under pressure.
  • Going slightly off topic, the best thing about an electrically heated shower is that the heat is only supplied at the point of use.
    If you prefer a shower to a bath, then why do you need a hot water tank?
  • Chris Pearson:
    Otherwise, every sink and basin would also need its own point-of-use heater.  And those wouldn't run on E7.
  • The high rated electric showers are often just too hot to use, "scalding" in fact, so many people only use them at a reduced heat setting anyway. A shower rated at just under 9kW is more than adequate in most cases. (Yes I am aware of shower internal, temperature regulation).
    Stored hot water pumped showers can run cold when all of the stored hot water has been used up.
    This house resembles one that I used to own. Do not overlook the fact that night storage heaters have inbuilt thermostats that cut out when the heaters are at a preset temperature so may not all be using current at the end of the charge cycle. This reduces the overloading risk.
  • I wanted to consider RCBOs instead of a dual RCD setup, but the cost may be prohibitive.
    An installation with R.C.B.O.s is much superior to a split load board and affords protection against nuisance tripping and loss of supply of many circuits in case of faults.
    R.C.B.O.s from C.P.C. are only about 15 squid each.
  • Assuming a full storage heater load of 13.6kW, a shower at about 10.0kW and the immersion heater and cooking as well, totalling about 30kW that equates to a load of about 125 Amps at 240 Volts with everything working at the same time.
    If the main fuse is a B.S. 1361 cartridge fuse rated at 60 Amps it will take about 2.5 hours to rupture, but it will run hot (not good at all). A 63 Amp. B.S. 88-3 fuse would last for about 30 minutes at full load. If the fuse is a B.S, 1361 type rated at 100 Amps it will take much longer to rupture if it ever does at all.