I have read many times about how it is beneficial to wire 4-20ma loops using twisted pair, however what if the wiring is 3 wire (i.e. +,- and signal)?
  • Does this mean that you simply use screened three core?

  • Does this mean you use two twisted pair and if so what one is the single?

Parents
  • The benefits of twisted pair are lost on a 3-wire loop device, as there are no two wires where the the currents are the same, but flow in opposite directions.


    3-core screened would be better.


    Basically, the current in the common wire should sum to the total current in the remaining power wire and the transmitter (signal) wire, so these three should be as close as possible and within the same cable.


    So, whilst 3-wire transmitters might be cheaper, they have their down-sides.
Reply
  • The benefits of twisted pair are lost on a 3-wire loop device, as there are no two wires where the the currents are the same, but flow in opposite directions.


    3-core screened would be better.


    Basically, the current in the common wire should sum to the total current in the remaining power wire and the transmitter (signal) wire, so these three should be as close as possible and within the same cable.


    So, whilst 3-wire transmitters might be cheaper, they have their down-sides.