I personally don't see the point in insulating internal walls.
mapj1:
depends rather on the stud wall - 12mm or 9mm board, spacing and interlocking of woodwork etc.
The Gyproc white book can be downloaded from here and has figures for attenuation for various constructions you can compare to the 45 dB figure in the AD.
whjohnson:
I personally don't see the point in insulating internal walls.
Chris Pearson:
Well, given the modern preference for open-plan living (not the case here) it seems that plenty of people can cope with other's noise.
If any wadding is to be put into the wall, then we potentially end up with Reference Method A, in which case the 2.5 mm2 cable is downgraded to 20 A.