Wouldn't the supply be lost as well as the means of earthing?
Yes, in the case of a broken PEN, the supply would be lost - or at least usually significantly reduced (depending on what remained connected to Earth upstream of the break) - but the broken PEN conductor & installation earthing system would still be pulled towards line voltage by other connected loads in the installation, and while the various pilot functions (often including the vehicle's check of the earth loop) might prevent the charge point's L&N contacts closing, the PE connection (other than in specifically open-pen detecting charge points) would usually remain solidly connected.
- Andy.
Wouldn't the supply be lost as well as the means of earthing?
Yes, in the case of a broken PEN, the supply would be lost - or at least usually significantly reduced (depending on what remained connected to Earth upstream of the break) - but the broken PEN conductor & installation earthing system would still be pulled towards line voltage by other connected loads in the installation, and while the various pilot functions (often including the vehicle's check of the earth loop) might prevent the charge point's L&N contacts closing, the PE connection (other than in specifically open-pen detecting charge points) would usually remain solidly connected.
- Andy.
Wouldn't the supply be lost as well as the means of earthing?
Yes, in the case of a broken PEN, the supply would be lost - or at least usually significantly reduced (depending on what remained connected to Earth upstream of the break) - but the broken PEN conductor & installation earthing system would still be pulled towards line voltage by other connected loads in the installation,
I think the truth of the matter is significantly more complex.
The answer is "Not necessarily" ... there are a few situations that would keep the "lights on full" as it were, chiefly because most PME distribution systems are three-phase:
(a) the balance on the network may well mean Neutral current is very low (or zero), in which case the touch potential to the general mass of Earth will be kept down. However, the balance can also be such that, on one or more phases, the voltage can still be significant enough to operate equipment, in fact within "normal" limits, with a hazardous touch potential on the supply neutral (and hence PE of the installation) with respect to the general mass of Earth - only one phase may see a "low voltage".
(b) There could be a sufficiently-low resistance of fortuitous connection back to the supply Neutral, through extraneous-conductive-parts, so that everything seems "normal" - and this again wouldn't necessarily lead to a high touch potential, that is until suddenly something changes.
(c) Even if the installation is upstream of a break, there are occasions when diverted neutral currents could occasionally cause a local rise of PE potential with respect to the general mass of Earth.