OMS:
Apostolos Kasinalis:
I think you can see why I am a bit reluctant to use PME on the EVC points although it is inside the building.
OK - if you decide to go for a TT supply to the EVC's how do you segregate the TT electrode from the earthy frame of the building which has PME for all the other services.
Consider if it would be safer making arrangements to connect the rebar under the vehicle areas to the MET and retaining PME to supply the EVC - what potentials would exist between the vehicle body and the floor slab that a person might actually bridge between hand and foot in either case
Regards
OMS
OMS:
Apostolos Kasinalis:
I think you can see why I am a bit reluctant to use PME on the EVC points although it is inside the building.
OK - if you decide to go for a TT supply to the EVC's how do you segregate the TT electrode from the earthy frame of the building which has PME for all the other services.
Consider if it would be safer making arrangements to connect the rebar under the vehicle areas to the MET and retaining PME to supply the EVC - what potentials would exist between the vehicle body and the floor slab that a person might actually bridge between hand and foot in either case
Regards
OMS