Unusual Earthing System

One of the Cahier Technique papers talked about an earthing system, which it described variously as cross between TT and TN-S or an 'impedance earthed TN-S' system, although I don't think either description is particularly accurate. Basically it suggests earthing the supply star point via an impedance, but then Earthing the consumer systems to the same electrode as the source:

66c3de7fa1842c6eefc0499bb3bad3a7-huge-notttnortn-s.png


As earth fault currents would be low, you'd need RCDs for ADS (just like a TT system), but the way the earthing is connected would seem to give a number of advantages over normal TT or TN systems. The most obvious perhaps is that exposed-conductive-parts remain at (or very close to) true Earth potential even during a L-PE fault - substantially reducing the risks of shock (even for the 5% of the population who aren't necessarily safe under normal ADS) - unlike a TN system where the point of the fault is likely to be at around half the line voltage, and in a TT system anything up to the full line voltage. It also less of an immediate issue if an RCD is a bit sticky or even fails to open altogether. They also claim less risk of damage or fire from L-PE faults than on TN systems - as the fault current is so much reduced.


So firstly what should this system be called? The impedance at the source is like an IT system - but the "T" would mean the consumer has their own earth electrode independent of the source's - which very specifically isn't the case here. Neither is the consumer's PE conductors directly connected to the system neutral which an "N" would usually indicate. As far as I know there isn't a letter to say the consumer's earth is connected directly to the supply's means of earthing (and not N) - maybe we could use "E" or "PE" for that - making it a IPE or IE system? I'm sure there are some better ideas out there.


My other thought was how would such an arrangement fair from the point of view of things like EMI or the effectiveness of SPDs - would it make any difference?


   - Andy.
Parents
  • In the British Isles, it is specifically banned by legislation for the LV systems in the Public Electricity Supply. It is widely used at 11kV and often at 33kV to reduce earth fault current, and therefore the cost of cables. At the higher distribution voltages, particularly on overhead networks, there is also impedance earthing using a Peterssen Coil. Here, the system can be stable while one phase is more or less earthed without excessive earth current. The issue is detection of a downed conductor, as it is important to know what the earth fault is. For this reason, the duration of the earth fault will be limited by the protection systems. 


    Regards,


    Alan.
Reply
  • In the British Isles, it is specifically banned by legislation for the LV systems in the Public Electricity Supply. It is widely used at 11kV and often at 33kV to reduce earth fault current, and therefore the cost of cables. At the higher distribution voltages, particularly on overhead networks, there is also impedance earthing using a Peterssen Coil. Here, the system can be stable while one phase is more or less earthed without excessive earth current. The issue is detection of a downed conductor, as it is important to know what the earth fault is. For this reason, the duration of the earth fault will be limited by the protection systems. 


    Regards,


    Alan.