This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Minimum Voltage at incoming supply point

Retired now and not up to date with reg’s since 16th. Helping advise a friend. Currently they have 100amp single phase supply and whilst the no load voltage is up at around 238 volts, as the circuit is loaded, voltage drops off substantially. Even with a load of 50 amps, ie, half the supply fuse rating, voltage is slightly below the -6% limit, at around 215 volts, further load simply pushes voltage significantly lower, and by extrapolating measured data, it would be nearer 170 volts with a load of 100 amps, is this acceptable? I plan measuring Ze and pfc this week as a guide perhaps to supply loop impedance and, which I suspect must be causing this excessive drop. I’m aware of the ESQCR reg’s although need to update myself, but are there any other regulations that apply?

Parents
  • It is possible that the supply is restricted to only 40 amps. Or is MEANT to be 40 amps and that someone has improperly fitted a larger fuse. Not very likely these days, but 40 amp supplies do still exist. I found a 25 amp service recently.

    The voltage might be just within tolerance at 40 amps.
Reply
  • It is possible that the supply is restricted to only 40 amps. Or is MEANT to be 40 amps and that someone has improperly fitted a larger fuse. Not very likely these days, but 40 amp supplies do still exist. I found a 25 amp service recently.

    The voltage might be just within tolerance at 40 amps.
Children
No Data