Minimum Voltage at incoming supply point

Retired now and not up to date with reg’s since 16th. Helping advise a friend. Currently they have 100amp single phase supply and whilst the no load voltage is up at around 238 volts, as the circuit is loaded, voltage drops off substantially. Even with a load of 50 amps, ie, half the supply fuse rating, voltage is slightly below the -6% limit, at around 215 volts, further load simply pushes voltage significantly lower, and by extrapolating measured data, it would be nearer 170 volts with a load of 100 amps, is this acceptable? I plan measuring Ze and pfc this week as a guide perhaps to supply loop impedance and, which I suspect must be causing this excessive drop. I’m aware of the ESQCR reg’s although need to update myself, but are there any other regulations that apply?

Parents
  • Or could just be a loose connection somewhere. I was asked to look at one house where 'the lights dimmed when the kettle was switched on' - loop readings were all over the shop but the give away was the audible 'crackling' sound coming from the DNO's cutout when the kettle was on. A call to the DNO with "my electrician says..." apparently brought a swift resolution.

      - Andy.
Reply
  • Or could just be a loose connection somewhere. I was asked to look at one house where 'the lights dimmed when the kettle was switched on' - loop readings were all over the shop but the give away was the audible 'crackling' sound coming from the DNO's cutout when the kettle was on. A call to the DNO with "my electrician says..." apparently brought a swift resolution.

      - Andy.