Minimum Voltage at incoming supply point

Retired now and not up to date with reg’s since 16th. Helping advise a friend. Currently they have 100amp single phase supply and whilst the no load voltage is up at around 238 volts, as the circuit is loaded, voltage drops off substantially. Even with a load of 50 amps, ie, half the supply fuse rating, voltage is slightly below the -6% limit, at around 215 volts, further load simply pushes voltage significantly lower, and by extrapolating measured data, it would be nearer 170 volts with a load of 100 amps, is this acceptable? I plan measuring Ze and pfc this week as a guide perhaps to supply loop impedance and, which I suspect must be causing this excessive drop. I’m aware of the ESQCR reg’s although need to update myself, but are there any other regulations that apply?

Parents
  • Former Community Member
    0 Former Community Member
    the current demand, by domestic standards is large, and includes heat-pumps for both house and pool, and these in particular are being adversely affected by the low voltage.


    Has to requirement to notify the DNO of the wish to connect a "disturbing load" over 2? kW and the consequences of "flicker" been rescinded?


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    the current demand, by domestic standards is large, and includes heat-pumps for both house and pool, and these in particular are being adversely affected by the low voltage.


    Has to requirement to notify the DNO of the wish to connect a "disturbing load" over 2? kW and the consequences of "flicker" been rescinded?


    Regards


    BOD