Minimum Voltage at incoming supply point

Retired now and not up to date with reg’s since 16th. Helping advise a friend. Currently they have 100amp single phase supply and whilst the no load voltage is up at around 238 volts, as the circuit is loaded, voltage drops off substantially. Even with a load of 50 amps, ie, half the supply fuse rating, voltage is slightly below the -6% limit, at around 215 volts, further load simply pushes voltage significantly lower, and by extrapolating measured data, it would be nearer 170 volts with a load of 100 amps, is this acceptable? I plan measuring Ze and pfc this week as a guide perhaps to supply loop impedance and, which I suspect must be causing this excessive drop. I’m aware of the ESQCR reg’s although need to update myself, but are there any other regulations that apply?

Parents
  • Its a non post, the poster just wants the DNO to do the calculations, we get it all the time. This is clearly an additional load, and we require a declaration. Perhaps he can come on here and tell us the calculations he has arrived at. I doubt we will hear of those though.


    Regards, UKPN
Reply
  • Its a non post, the poster just wants the DNO to do the calculations, we get it all the time. This is clearly an additional load, and we require a declaration. Perhaps he can come on here and tell us the calculations he has arrived at. I doubt we will hear of those though.


    Regards, UKPN